Inside Metrology
Andreas Eberhard  |  08/10/2009
Andreas Eberhard’s picture
Voltage Sag Testing for Industrial Equipment
A new power quality measurement technology
Modern equipment can be sensitive to brief disturbances on utility power mains. Electrical systems are subject to a wide variety of power quality problems that can interrupt production processes, affect sensitive equipment, and cause downtime, scrap, and capacity losses. The most common disturbance, by far, is a sag: a brief reduction in voltage lasting a few hundred milliseconds.
Sags are commonly caused by fuse or breaker operation, motor starting, or capacitor switching, but they are also triggered by short circuits on the power distribution system caused by events such as snakes slithering across insulators, trenching machines hitting underground cables, and lightning ionizing the air around high-voltage lines. Many utilities report that 80 percent of electrical disturbances originate within the user’s facility.
A decade ago, the solution to voltage sags was to try to fix them by somehow storing enough energy and releasing it onto the AC mains when voltage dropped. Some of the old solutions included an uninterruptible power supply (UPS), flywheels, and ferroresonant transformers.
More recently, engineers have realized that voltage sag is really a compatibility problem with at least two classes of solutions: You can improve the power or you can make the equipment tougher. The latter approach is called “voltage sag immunity,” and has gained importance around the world.
Figure 1. Immunize your products and facilities. Voltage sag immunity testing has been common in the semiconductor industry for years and has proved its economic value. New IEC standards for voltage sag immunity will expand this kind of testing and certification to other industries.
Standards developed
There are three main primary voltage sag immunity standards: IEC 61000-4-11, IEC 61000-4-34, and SEMI F47. There are others in use—such as IEEE 1100, CBEMA, ITIC, Samsung Power Vaccine, international standards, and MIL-STD—but the first three seem to have the widest acceptance in the marketplace. (IEC is the International Electrotechnical Commission, SEMI is the Semiconductor Equipment and Materials Institute, CBEMA is the Computer Business Equipment Manufacturers Association, ITIC is the Information Technology Institute Council, and MIL-STD is the U.S. Defense Department’s specification.)
IEC 61000-4-11 and IEC 61000-4-34 are a closely related set of standards that cover voltage sag immunity. IEC 61000-4-11 Ed. 2 covers equipment rated at 16 amps per phase or less while IEC 61000-4-34 Ed. 1 covers equipment rated at more than 16 amps per phase. The latter was written after IEC 61000-4-11, so it seems to be more comprehensive.
SEMI F47 is the voltage sag immunity standard used in the semiconductor manufacturing industry, where a single voltage sag can result in the multi-million-dollar loss of product if a facility is not properly protected. The semiconductor industry has developed specifications for its manufacturing equipment and for components and subsystems in that equipment. Enforcement is entirely customer-driven in this industry, as semiconductor manufacturers understand the economic consequences of sag-induced failures and generally refuse to purchase new equipment that fails the SEMI F47 immunity requirement. SEMI F47 is currently going through its five-year revision and update cycle.
All three standards specify voltage sags with certain depths and durations for the equipment under test (EUT). For example, a specification may state 70 percent of nominal for 500 milliseconds. The percentage is the amount of voltage remaining, not the amount that is missing. Each standard specifies pass-fail criteria for EUT when a voltage sag is applied; the IEC standards have a range of pass-fail criteria, but the SEMI F47 standard is more explicit (figure 2).
Figure 2. Playing through. A typical example of a voltage sag ride-through curve compared with the SEMI F47 specification commonly used in the semiconductor industry.
A different kind of testing
In contrast to most other emissions and immunity testing, voltage sag testing requires the engineer to control and manipulate all of the power flowing into the EUT. For smaller devices such as personal computers, this is not a great challenge. But for larger industrial equipment, perhaps rated at 480 volts three-phase at 200 amps per phase, with an expected inrush current of 600 amps or more, the test engineer must be prepared for
Common failure mechanisms due to voltage sags
The most common failure mechanism is lack of energy. This can manifest itself in something as simple as insufficient voltage to keep a critical relay or contactor energized or something as complex as an electronic sensor with a failing power supply giving an incorrect reading, which would cause EUT software to react inappropriately (Figure 6).
Figure 3. Anatomy of voltage sag. To test a new product, a voltage sag is introduced in the power source (a). The waveform, which was about 40 amps peak before the sag in this example, then increases to 450 amps peak after the voltage sag (b). The same current, this time expressed as an RMS value, is shown. The next graph shows the same current, this time as an RMS value. Before the sag, it was about 23 amps RMS (this equipment was rated at 30 amps), but after the sag the current increased to 175 amps RMS. This behavior is not unusual (c). The final graph shows the output of a DC supply during this sag (d).
The second most common failure mechanism, surprisingly, occurs just after the sag has finished. In such cases, all of the bulk capacitors inside the EUT recharge at once, causing a large increase in AC mains current. This increase can trip circuit breakers, open fuses, and even destroy solid-state rectifiers. Most design engineers correctly protect against this inrush current during power cycling, but many do not consider the similar effects of voltage sags. Be careful when the test procedure is developed; if you use a sag generator that lacks sufficient current capability it will incorrectly pass the equipment if there is insufficient current available to blow a fuse or trip a circuit breaker in a half-cycle.
Another common EUT failure mechanism occurs when a sensor detects the voltage sag and decides to shut down the EUT. In a straightforward example, a three-phase EUT might have a phase-rotation relay that incorrectly interprets an unbalanced voltage sag as a phase reversal and therefore shuts down the EUT. A more atypical example would be if you had an airflow sensor mounted near a fan, it detected that the fan had slowed down momentarily, and the equipment software misinterpreted the message from this sensor as indicating that the EUT cooling system had failed. In this case, a software fan failure signal delay is the solution to improve sag immunity.
One more typical EUT failure mechanism involves an uncommon sequence of events. For example, in one case, a voltage sag was applied to the EUT and its main contactor opened with a bang. But further investigation revealed that a small relay, wired in series with the main contactor coil, actually opened because it received an open relay contact from a stray water sensor. That sensor, in turn, opened because its small 24-VDC supply output dropped to 18 V during the sag. The solution was an inexpensive bulk capacitor across the 24-VDC supply.
Many other failure mechanisms can take place during voltage sags. The question to the test engineer will always be: How do we fix this problem? Usually, there is a simple, low-cost fix once the problem is identified.
Embedded Power Quality Monitoring
There is a new way to increase the reliability of products due to common power quality and voltage sag problems. How about making the product more intelligent—so it can react depending on severity of the voltage sag problem?
The new trend is toward embedded and intelligent power quality monitoring, and you will see more and more of such permanently installed power quality monitors on a product level. The new generation of power quality monitor, such as the PQube from Power Standards Labs shown in figure 4, have the same functionality and features as well known, but expensive, power quality instruments. Such instruments are typically used on a facility level and are much too expensive, and course way too big, to integrate and design into products. This new embedded technology has an advantage over facilities-type instruments, in that power quality problems and energy consumption can be evaluated directly within the product or machine.  By packaging the power quality monitor in a standard 35 mm DIN-rail circuit breaker package, installation is greatly simplified. The PQube detects any kind of power problems on the AC lines and can communicate directly with the product, machine, or facility personnel.
Figure 4: Picture of latest low-cost PQube—Power Quality and Energy Monitor for permanent installation and integration
The version shown in figure 4 has Ethernet connectivity (and includes a web server, an FTP server, and an e-mail generator), wireless radio connectivity, and a modem connection. However, it is optimized to function without connectivity – it can easily store a year’s data on a removable SD memory card. Following the software model of a digital camera, the PQube requires absolutely no software. Just as connecting a digital camera to your computer immediately puts pictures in a folder on your disk drive, the same is true for power quality data in this application.
With the ever-increasing use of sophisticated controls and equipment in industrial, commercial, institutional, and governmental facilities, the continuity, reliability, and quality of electrical service has become extremely crucial to many power users. The power hardly gets better in the future, so the ultimate goal for any product manufacturer is to make its product immune to voltage sags. Like all modern cars should be able to drive through regular bumps on the road, every electrical product should be able to ride-through any regular voltage sags that will occur—despite of the best power that a facility can provide.
Andreas Eberhard
Andreas Eberhard is member of various power quality standard committees around the world. He has more than 10 years of experience in product compliance based on international standards. He is vice president of technical services at Power Standards Labs and can be contacted at aeberhard@powerstandards.com, or Tel ++1-510-522-4400